Scenario:
I'm analyzing an existing structure that is a 3-story high-end fitness club. For example, the club has a pool area on the lower level, and has squash courts, one full size basketball court (no seating), large open areas for various lifting equipment on the upper floors. Drawings state a design LL of 100psf was used. There is no indication that vibration was a consideration in the design.
Questions:
1) Is a "fitness center" a "gymnasium"?
2) What is the most appropriate live load to use for fitness centers? I feel that 100psf is adequate and that local checking is required for heavy equipment loads based on other eng-tips forums(squat racks, etc).
3) Do you consider fitness centers as "assembly" areas or uses?
4) Related to question 3), what about live load reduction for girders and columns? Per ASCE 7-16, live loads that exceed 100psf shall not be reduced (4.7.3). In this case, I am not exceeding 100psf so I should be able to reduce the live loads at least for columns supporting multiple floors. It may prove to not be conservative to implement for floor beams, or even girders, based on heavy localized areas of equipment. However, per ASCE 7-16, live loads shall not be reduced in assembly uses (4.7.5). Further, ASCE 7-16, Table 4.3.1 for gymnasiums it states live load reduction and multiple-story live load reduction is NOT permitted.
I'm analyzing an existing structure that is a 3-story high-end fitness club. For example, the club has a pool area on the lower level, and has squash courts, one full size basketball court (no seating), large open areas for various lifting equipment on the upper floors. Drawings state a design LL of 100psf was used. There is no indication that vibration was a consideration in the design.
Questions:
1) Is a "fitness center" a "gymnasium"?
2) What is the most appropriate live load to use for fitness centers? I feel that 100psf is adequate and that local checking is required for heavy equipment loads based on other eng-tips forums(squat racks, etc).
3) Do you consider fitness centers as "assembly" areas or uses?
4) Related to question 3), what about live load reduction for girders and columns? Per ASCE 7-16, live loads that exceed 100psf shall not be reduced (4.7.3). In this case, I am not exceeding 100psf so I should be able to reduce the live loads at least for columns supporting multiple floors. It may prove to not be conservative to implement for floor beams, or even girders, based on heavy localized areas of equipment. However, per ASCE 7-16, live loads shall not be reduced in assembly uses (4.7.5). Further, ASCE 7-16, Table 4.3.1 for gymnasiums it states live load reduction and multiple-story live load reduction is NOT permitted.