Hello,

I'm designing a sprinkler system for a residential building (light hazard). However, this building has an unheated parking (ordinary hazard I). Running the hydraulic calculations, I find out that I don't have enough water to supply my system (the public main only provides me with 500 GPM and I need around 660 GPM - 410GPM for my sprinklers and 250 GPM for the outside hose allowance). So I have to provide a tank, right? How should I size my tank? 660 or 160 GPM for 60 MIN? And Where this supply will be added to my system? Thanks in advance.
 
It depends on the local codes how you handle this.

= = = = = = = = = = = = = = = = = = = =
P.E. Metallurgy, Plymouth Tube
 
Correct, local code and the underwriters.

It is a capital mistake to theorise before one has data. Insensibly one begins to twist facts to suit theories, instead of theories to suit facts. (Sherlock Holmes - A Scandal in Bohemia.)
 
I don't know where the deficiency is occurs, however, you may want to look into a closed water loop to the sprinkler system alarm check valve or a closed main loop feeding the branch lines.
 