Hi All,
I have a situation where I have 22 meter columns that are required to abide by a 120 min fire. In accordance with CL 5.6.4 General tabular method to determine structural adequacy of columns a slenderness limit under the fire condition is <30. My columns are running at approximately 40.
Due to the limitations of AS3600 I have adopted the 500 degree isotherm approach from Eurocode 2 which is referenced in AS3600 Clause 5.3.1 General Performance Criteria Notes 1 & 2.
When we go to the Eurocode 2 there is additional requirements for spalling not covered under AS3600, for instance high strength concretes or when the axis distance of the bar is greater than 70mm from the edge additional mesh is required for spalling.
The question is, can we waive these spalling requirements whilst adopting EC2 500 Degree Isotherm Method?
Thanks in advance.
I have a situation where I have 22 meter columns that are required to abide by a 120 min fire. In accordance with CL 5.6.4 General tabular method to determine structural adequacy of columns a slenderness limit under the fire condition is <30. My columns are running at approximately 40.
Due to the limitations of AS3600 I have adopted the 500 degree isotherm approach from Eurocode 2 which is referenced in AS3600 Clause 5.3.1 General Performance Criteria Notes 1 & 2.
When we go to the Eurocode 2 there is additional requirements for spalling not covered under AS3600, for instance high strength concretes or when the axis distance of the bar is greater than 70mm from the edge additional mesh is required for spalling.
The question is, can we waive these spalling requirements whilst adopting EC2 500 Degree Isotherm Method?
Thanks in advance.