FIRE RATING FOR TRANSFORMER VAULTS OF 13.5 KV AND ABOVE? 1

Status
Not open for further replies.

vaaoc1425

Electrical
Nov 14, 2006
25
I would like to know what is the Fire Rating Criteria is for 13.5 KV and above Network Transformer Vault Wall Construction in the US. If it is addressed NEC [National Electrical Code in US], I cannot find it. Any Electrical or/and Building Standard code that address matter in the US will be greatly appreciated..
 
Replies continue below

Recommended for you

In the US, this will be a Fire Code issue. Refer to NFPA. You might want to post a question in the NFPA forum on this website. The answer will likely be dependent on the location of the vault and the type of building it is serving.

Is this an electric utility system network vault? If so, the NEC will not be applicable (in any respect).

 
3 hour rating, unless sprinklered. See NEC 450.42.

Alan
----
"It’s always fun to do the impossible." - Walt Disney
 
Doh! I should have remembered that - Thanks Alan.

Dave
 