I have a ESFR system that requires 1370 gpm from the pump. The supply is 73 static and 44 residual. Pleanty of water to make this happen. Problem is, the municipality wants to keep the supply line at 20 psi or greater. This only gives us 1320 gpm. They are suggesting we put a valve in to limit our suction. By our calculations our demand would put the suply pressure in the 14 - 15 psi range. Have any of you ran into a similar situation like this and how did you resolve it short of a storage tank?
I just can't find the logic of the 20 psi minimum requirment. 45% just seems to be a high saftey factor