waross, I'm just trying to help: the start-up voltage drop has to be 15% or less, per the Fire Pump Standard (USA):
NFPA 20, 2010 edition: Article 9.4 "Voltage Drop."
There is an exception for bypass operation with a VFD, but if we're talking across-the-line, the original timm333 post is correct: voltage drop is limited to 15%.
timm333: you might consider a VFD. I was able to easily start a VFD-driven fire pump, 125 HP, using "only" a 235 KW diesel generator. When I was trying to size the generator with manufacturer's software, some of their selections were as high as 500 KW. I finally got together with a sales rep who worked with me to get the KW down, using an over-sized alternator and some other techniques. The job worked just fine. If you're interested, here is contact info for that sales rep: