Hi everyone,
The reason I am consulting you is to ask if you know if there is any limitation or restriction given by NFPA 20 or NFPA 70 (NEC) for the power supply configuration of an electrical driven fire pump; I mean if it matters if it is Wye solidly grounded or Wye grounded with a NGR.
I have read these two standards and I have not found anything but I am not 100% sure.
In our design there is a 460 V 250 hp motor (fire pump) and a 460 V 5 hp (jockey pump) fed from a 1250 kVA 13.8/0.48 kV transformer Delta-Wye. The question will be if it matters if the Wye side is solidly gorunded or limited through a 5 A NGR - is there anything that rules this? In any case a ground fault protection will not be installed as per NFPA requirements.
Thanks and regards,
The reason I am consulting you is to ask if you know if there is any limitation or restriction given by NFPA 20 or NFPA 70 (NEC) for the power supply configuration of an electrical driven fire pump; I mean if it matters if it is Wye solidly grounded or Wye grounded with a NGR.
I have read these two standards and I have not found anything but I am not 100% sure.
In our design there is a 460 V 250 hp motor (fire pump) and a 460 V 5 hp (jockey pump) fed from a 1250 kVA 13.8/0.48 kV transformer Delta-Wye. The question will be if it matters if the Wye side is solidly gorunded or limited through a 5 A NGR - is there anything that rules this? In any case a ground fault protection will not be installed as per NFPA requirements.