NEC 695-6 is specifically about "Power Wiring". It does not address the control wiring. The only thing that it enforces is that no matter what, the pump must run. Remote alarms are important, but not critical as long as the pump continues to operate. All the subsecttions of 695 deal with the power feed to the pump. If you are running the feeder in the required fire rated enclosure, you can include a conduit for controls, they rarely go to the same place though.
As a side note, are you familiar with the copper bound fire rated fire pump feeder manufactured by "Pyrotenax"? I have found that this saves a lot of time effort and cost. It's costly, but a bargain when compared to the cost of providing rated shafts, encased conduit, etc....