Fire Hose Valve Height?

Status
Not open for further replies.

Mhilliar

Mechanical
Joined
May 13, 2016
Messages
1
Location
US
Anyone know what the requirements are for the height of a hose valve station on a fire stand pipe and where I can find said code?
 
NFPA 14 is your friend:
7.3 Locations of Hose Connections.
7.3.1* General.
7.3.1.1 Hose connections and hose stations shall be unobstructed and shall be located not less than 3 ft (0.9 m) or more
than 5 ft (1.5 m) above the floor.

Travis Mack
MFP Design, LLC
"Follow" us at
 
Possibly in NFPA 14

Will look
 