May 13, 2016 #1 Mhilliar Mechanical Joined May 13, 2016 Messages 1 Location US Anyone know what the requirements are for the height of a hose valve station on a fire stand pipe and where I can find said code?
Anyone know what the requirements are for the height of a hose valve station on a fire stand pipe and where I can find said code?
May 13, 2016 #2 TravisMack Mechanical Joined Sep 15, 2003 Messages 1,777 Location US NFPA 14 is your friend: 7.3 Locations of Hose Connections. 7.3.1* General. 7.3.1.1 Hose connections and hose stations shall be unobstructed and shall be located not less than 3 ft (0.9 m) or more than 5 ft (1.5 m) above the floor. Travis Mack MFP Design, LLC http://www.mfpdesign.com"Follow" us at https://www.facebook.com/pages/MFP-Design-LLC/92218417692 Upvote 0 Downvote
NFPA 14 is your friend: 7.3 Locations of Hose Connections. 7.3.1* General. 7.3.1.1 Hose connections and hose stations shall be unobstructed and shall be located not less than 3 ft (0.9 m) or more than 5 ft (1.5 m) above the floor. Travis Mack MFP Design, LLC http://www.mfpdesign.com"Follow" us at https://www.facebook.com/pages/MFP-Design-LLC/92218417692
May 13, 2016 #3 cdafd Specifier/Regulator Joined Aug 18, 2005 Messages 2,953 Location US Possibly in NFPA 14 Will look Upvote 0 Downvote