Consider the following quote from the city water department:
"In the fire flow test you had done on the fire hydrant... they flowed the 2 1/2" port and it showed a result of 1,140 gpm at 58 psi. Extending the graph out to the end, you were showing a fire flow of 3800 gpm at 25 psi. Knowing my experience with fire flow tests, and what I know about non looped systems, I believe the top end of the graphs for flowing higher volumes is not accurate when flowing the 2 1/2" port. The 4" port is more accurate, and therefore, I had the fire flow test repeated flowing the 4" port to flow a larger volume of water. The results of this test are much lower, and more accurately depicts what happens when the flows get higher in the dead end 12" main…the static pressure was 64 psi, and the hydrant flowed 1,718 gpm at 42 psi, or 2341 gpm at 25 psi which is 2,498 gpm at 20 psi, far short of the 3,000 gpm needed for fire flows...”
Any thoughts, comments why the 2 ½” test and the 4” test should be so different – 3,800 gpm vs. 2,341 gpm? Any recommendations on how we can proceed given the apparent inadequate water system?