Rookie2
Civil/Environmental
- Nov 15, 2003
- 75
Hi,
I am working on a residential subdivision where we are tying into an existing waterline that looks something like this-
exhyd1 exhyd2 exhyd3
0----------------0---------------0
Our site is adjacent to existing hydrant 2. In order to perform our fire flow calculations (1000gpm at 20psi required), the municipality provided us a flow test with the flow measured at hydrant 2, and pressure readings taken at hydrant 3. The existing waterline of course is part of a much larger system and we don't know how much of the flow at hydrant 2 is coming from either direction (hyd3 or hyd1).
We need to know this to accurately calculate the friction losses in order to calculate the available pressure at hyd2. This is a 6" line so friction losses are a major factor.
In order to eliminate the question of which direction the flow is coming, we are thinking of asking for the flow and pressure to be measured at hydrant 2. These are multiple outlet hydrants and the pressure would me measured at one outlet and flow at another. I've read about this testing method at and from what I've read I believe this method would be conservative, because there is additional headloss due to the fire hydrant assembly itself. Measuring flow at one hydrant and pressure at another eliminates this headloss.
I just wanted to get other opinions on this. Is this an acceptable way to do this? If not what is a better way to go about it?
I hope I've asked this question clearly, any input would be greatly appreciated.
Thanks
I am working on a residential subdivision where we are tying into an existing waterline that looks something like this-
exhyd1 exhyd2 exhyd3
0----------------0---------------0
Our site is adjacent to existing hydrant 2. In order to perform our fire flow calculations (1000gpm at 20psi required), the municipality provided us a flow test with the flow measured at hydrant 2, and pressure readings taken at hydrant 3. The existing waterline of course is part of a much larger system and we don't know how much of the flow at hydrant 2 is coming from either direction (hyd3 or hyd1).
We need to know this to accurately calculate the friction losses in order to calculate the available pressure at hyd2. This is a 6" line so friction losses are a major factor.
In order to eliminate the question of which direction the flow is coming, we are thinking of asking for the flow and pressure to be measured at hydrant 2. These are multiple outlet hydrants and the pressure would me measured at one outlet and flow at another. I've read about this testing method at and from what I've read I believe this method would be conservative, because there is additional headloss due to the fire hydrant assembly itself. Measuring flow at one hydrant and pressure at another eliminates this headloss.
I just wanted to get other opinions on this. Is this an acceptable way to do this? If not what is a better way to go about it?
I hope I've asked this question clearly, any input would be greatly appreciated.
Thanks