why is the room required to have a ceiling???""
To provide a Smokeproof enclosure??
detectors are located aprox 3ft from the exterior wall on the lower portion of the Pitched roof."" I have attach a Picture of the Building (small dots), I hope this helps.
does nto sound right, but would have to see the entire building before making a call, does the buiilding have a fire sprinkler system???
No, it does not have a sprinkler.
so how are you connected with this???inspector, Inspector
worker, fire alam company
Is this room also open to other space which happen to be the space above the hung ceiling for other rooms? Yes
In other words, does the walls of this room go all the way up to the pitched roof or not?
No the walls do not go up to the pitched roof.
That makes a difference. If they do, you need detectors near the peak of the roof, per NFPA. If not, you need to first find out why there is no ceiling.
Not sure why there is no ceiling. Building owner thouht it was legal.
Thanks