Nov 2, 2005 #1 ELEcontrol3e Electrical Joined Apr 26, 2005 Messages 51 Location US Does fire protection have to extend up from the drywall, completely covering the gaps between the roofing deck and interior wall. Which NFPA code covers this? Thanks in advance.
Does fire protection have to extend up from the drywall, completely covering the gaps between the roofing deck and interior wall. Which NFPA code covers this? Thanks in advance.
Nov 2, 2005 1 #2 TravisMack Mechanical Joined Sep 15, 2003 Messages 1,776 Location US If you have a concealed combustible space, you are required to protect it, barring a few exceptions. This is found in NFPA 13. Upvote 0 Downvote
If you have a concealed combustible space, you are required to protect it, barring a few exceptions. This is found in NFPA 13.