Scotty & mgtrp, yes it is real. The company is owned by SERGI, but it is still in it's infancy. I installed that rupture disk system at a pumped storage site in NJ a few years ago. The 129 MVA shell form transformer was built on the roof of the control building right on the reservior. They didn't want a deluge system because washing the oil into the reservior would be an environmental issue. Fire walls wouldn't protect the building. This seemed to be the only viable option. I can't explain why no pictures, but I have some I can Email out.
The company had video and much documentation of tests and three or four successful 'activations' from other customers.
The company offers a warranty as cost of a replacement transformer if it fails. Of course, if it does fail, the loss of revenue will likely far outweight the cost of a new transformer.
I can give the contact information of the people at the plant where this is installed, but I'm not posting it here. I also have many pictures somewhere. If anyone wants to know the details on this, they are welcome to contact me directly.
-Alex
------------------------------------------------------------------------