I am replacing an existing fire alarm panel with a new fire alarm panel and want to extend the existing fire alarm circuits to the new panel location. Is it acceptable to splice the existing fire alarm circuits? I vaguely recall somehwere that splicing fire alarm cable is not allowed but cannot find the code reference.
thanks.
 
Replies continue below

Recommended for you

have seen it done normally they gut the old box and use it as a junction box. I think the rule is if you splice you must use a junction box.
 
nfpa 72 says to meet nec 70
 