Field welding on hydro-carbon pipeline?

Status
Not open for further replies.

11echo

Petroleum
Jun 4, 2002
444
I witnessed a field weld on a semi large hydro carbon pipe line (12" - 18") where the welders inserted a "balloon" on a lanyard, inflated it to isolate the hydro carbon vapors in the line, and to further isolate any vapors a synthetic-base mud was mixed and liberally spread at the edge of the balloon and pipe wall. I remember this mud was very slippery, and had a tenancy to fleck off as it dried (welding was done when the mud was wet). This was some time ago, and I have forgotten what the mud was? ...Drilling mud? ...or some specialty mud? Anybody know?
 
Replies continue below

Recommended for you

Sounds like Drilling Mud to me.

If your future needs are just for a branch connection, it would be safer to use the procedure set forth in API-570, and do the welding with flow in the pipe.

Fumes plus air = explosion. Note that the 'mud' was drying out and loosing its seal during this operation. Too risky for me.

Welding heat on the OD of a line with flowing hydrocarbon [or any liquid] = cool, fast-freezing weld and no chance of going "BOOM".
 
Unfortunately that's not the case here. We have to tie-in to existing small diameter piping (3"), so I can't maintain any flow through the lines. Also there are no isolation valves or points on the existing lines to "block" any vapors. What I was hoping to do was cold cut the lines, isolate any vapors, and weld on flanges for a tie-in point. However I will look into API-570 and see if there is another option. THX!
 
For a tie-in, use either a "whisper purge" of natural gas, or propane. When the O2 level hits 0.0% and the LEL is off-scale, you are ready to weld. Weld uphill on the root, with the gas flames above the weld puddle. Have a 3/4 or 1" open nipple on the line, at the top, near your buttweld. This will relieve the pressure when the root is welded shut. As long as you have flames -- root gap, then at the nipple -- you have proof of a "too rich to burn" atmosphere inside your pipe. Gas companies use this method regularly.

If the buring whisper purge is too exciting for your Safety dept, you can use a Freeze Plug. Insert two inflatable bladders [plumbers drain plugs] into your line about 2-3 diameters apart. Leave a tube at the top and a hose at the bottom of the outer bag. Fill through the hose, until ALL the air is purged from between your bags -- 100% full of water. Now have somebody like TEAM Industrial put the freeze jacket and thermocouples on your line and freeze the water. As long as the thermocouples show 0-deg F or colder, the ice plug is structural, not just sealed. You should be able to hydro against a 3" Sch40 2-diameter freeze3 plug at 500 psig.

I have done 200 psig on a 20" line, and 3100 psig on a 1" line. Ice is amazing stuff.
 