A lot of 12,000 volt systems here is the U.S., such as the one that Cleveland Public Power has, are 6,900Y12,000 volts solidly grounded at the supply substation that steps down from say 138,000 volts. The distribution transformers are still connected phase to phase. On Cleveland Public Power's 12,000 volt system quite a few circuits do have a full size neutral but it is only used as a equipment grounding conductor, not to run any loads.
On these systems ferroresonance does not happen as much as on a 12,000 volt system where the only "grounding" is through the capacitance to ground.
The reason why the Russians invented the zig-zag set was to convert 3-wire ungrounded transmission and distribution to solidly grounded wye without having to replace existing supply transformers.
Both solidly grounded wye systems and resistance grounded 3-wire systems have a lot of advantages over ungrounded systems. On resistance grounded systems the grounding resistor is connected to the neutral of a wye source or a zig-zag set or on the secondary of a grounding transformer.