I am looking at a small storm shelter within a larger building. I am designing per
FEMA 361. I am considering reinforced masonry for the walls. When designing the
MWFRS using ASD method, I know that I use .6W in all of the load combinations.
When designing the reinforcing in the walls for out of plane loading, can I use .6W
of the component & cladding wind pressure?
Also, if I go with reinforced concrete, using the strength method, I know that I replace
1.6W with 1.0W for all load combinations. Can I also use 1.0W with the C&C wind load
when designing for out of plane loading?
It seems to me that for extreme wind, the calculated C&C wind pressure is the ultimate
value, and does not get factored up for the strength method, and actually gets reduced for
the ASD method.
Am I interpreting this correctly?
FEMA 361. I am considering reinforced masonry for the walls. When designing the
MWFRS using ASD method, I know that I use .6W in all of the load combinations.
When designing the reinforcing in the walls for out of plane loading, can I use .6W
of the component & cladding wind pressure?
Also, if I go with reinforced concrete, using the strength method, I know that I replace
1.6W with 1.0W for all load combinations. Can I also use 1.0W with the C&C wind load
when designing for out of plane loading?
It seems to me that for extreme wind, the calculated C&C wind pressure is the ultimate
value, and does not get factored up for the strength method, and actually gets reduced for
the ASD method.
Am I interpreting this correctly?