Baswm
Electrical
- Jul 26, 2009
- 3
A 40 KVA AC Generator, 400 Hz, 3 phase 115V, 6000 rpm.
Reading the General Specification sheet, Under Feeder Fault, it says THE SYSTEM SHALL PROVIDE FOR THE GENERATOR TO BE DEENERGIZED AND DISCONNECTED FROM THE LOAD BUS WHEN THE FAULT CURRENT ON ANY PHASE EXCEEDS 25 AMPERES.
I took that to mean if I have no load on phase A or B, and I put a variable load on phase C and adjust it so the current increases. When it exceeds 25 Amps, the GCU should take the generator off line. I measured up to 50 amps on phase C and nothing on Phase A or B and the Generator was still going strong.
If I short two phases together or any phase to neutral, the Generator goes off line after 6 seconds.
How do I check for feeder fault?
Reading the General Specification sheet, Under Feeder Fault, it says THE SYSTEM SHALL PROVIDE FOR THE GENERATOR TO BE DEENERGIZED AND DISCONNECTED FROM THE LOAD BUS WHEN THE FAULT CURRENT ON ANY PHASE EXCEEDS 25 AMPERES.
I took that to mean if I have no load on phase A or B, and I put a variable load on phase C and adjust it so the current increases. When it exceeds 25 Amps, the GCU should take the generator off line. I measured up to 50 amps on phase C and nothing on Phase A or B and the Generator was still going strong.
If I short two phases together or any phase to neutral, the Generator goes off line after 6 seconds.
How do I check for feeder fault?