Fault Location for Phase to Phase Fault

Status
Not open for further replies.

breadboard

Electrical
Joined
May 27, 2012
Messages
11
Location
US
When calculating the fault impedance for a C-A phase fault I am taking Vca/Ica to get Zca ( I am also assuming zero fault resistance). Is that the total loop impedance or is that the one way impedance to the fault? It seems to be the loop impedance to me but from what sources I have read they all imply it is the one way impedance.
 
ZT = TOTAL IMPENDANCE

VA = VC - IC*ZT
VC = VA - IA*ZT

VA - VC = (VC-VA) - (IC-IA)*ZT

2*(VA-VC) = -(IC-IA)*ZT

2*(VA-VC) = (IA-IC)*ZT

2*(VA-VC)/(IA-IC) = ZT

VAC/IAC = ZT/2

ZT/2 = half of the total loop impedance
 
Thank you for the clarification I understand now.
 