I prefer the MVA method. Calculate the short circuit MVA of each branch and combine them as admittances.
Utility MVA = 250 = MVAutil
Transformer MVA = MVA rating/Zpu =1.5MVA/.06 = 25 MVA
= Maximum short circuit to the transformer terminals if the primary is connected to an infinte bus.
Combine the MVA's. As admittances, series connected MVA's combine like resistances in parallel. Parallel MVA's add.
1/MVAsc = (1/MVAutil) + (1/MVAtx) = 1/250 +1/25 = 0.044.
MVAsc = 1/0.044 = 22.73 MVA.
At 415V, Isc = 22.73 MVAx 10^6/(415V x 1.732) =31,623 Amps 3 phase, nominal voltage.
For the 105% voltage factor, mulitply by 1.05 = 33,204.
For the fault level with an infinite bus I = 25MVAx10^6/(415V x 1.732)= 34,781A
As stated in the previous post, different X/R ratios can affect the acuracy of this method.