Fault Current through Armour? 1

Status
Not open for further replies.

rail1996

Electrical
Oct 29, 2003
14
I have been asked to calculate the fault current that flows through the armour of a power cable. Can someone please tell me how this is differ from the traditional line-earth fault calculations?
 
Replies continue below

Recommended for you

I think there is no difference at all. As long as the cable with armor is correctly modeled, the line-to-earth fault current resulting from the traditional calculations will be the same fault current flowing through the cable armor.

God bless!

 
It would be the same unless there is a parallel path to the armor, such as a ground wire or cable shield, in which case some of the fault current may flow in those.
 
If the armor is grounded at both ends, there will be parallel paths, making the modelling difficult.
 