I have come a across a design where a 65MVA, 66/22kV trfr was specified by a certain party to as follows:
rated short time withstand current @22kV = 12kA
rated peak withstand current @22kV = 30.6kA
I was tasked to do the IEC 60909 fault studies at the trfr 22kV bus and came up with the following:
Ik" = 11.22kA @22kV
Ip = 31.8kA @22kV
I pointed out to the engineer that specified the trfr that the rated peak current is less than the calculated value and that there is <10% margin between rated short time withstand current and Ik. He proceeded to contact the trfr manufacturer who said it was ok. But I have grave misgivings as the manufacturer representative is from an Asian background, has poor English and he actually got some of the parameters mixed up. I am thus not confident that the manufacturer clearly understood the question and implications.
The engineer shrugged his shoulders, said the manufacturer said it was okay and walked away. Client knows nothing about this.
I feel there is no margin of safety to allow for future increase in fault levels and if the trfr is on maximum tap when the 22kV fault occurs the fault current is even higher.
I was asked by the client to assist with the project doing the protection study but feel that it is my duty to inform the client that a trfr will be put into service soon that is not properly rated for the potential fault current duties. The client is not electrical and relies on his consultants.
Any comments? What are considered acceptable design margins for power trfrs fault ratings and potential fault current duties?
Thanks.
Ik" = 11.22kA @22kV
Ip = 31.8kA @22kV
Thanks.