x05sween
Electrical
- Jun 17, 2013
- 2
When calculating the three phase fault currents in a power network, should a protection device be considered in limiting the current? Let me explain a little more.
At the power station, there are 12 generators that are connected on two separate buses (6 on each) that are inter-tied by a CLIP (current limiting protector). This CLIP works as a fuse and will operate at, lets say, 3kA. This will reduce the fault current at the power station and throughout the network. The clip can also be disconnected in order to operate as two independent buses. There are 2 feeders connected on each side of the bus and do not connect with each other downstream.
So when performing the maximum 3 phase fault calculations, should I be using the fault contribution for only the generators on the same side as the feeder? I am concerned because a busbar downstream is rated at 30kA for 1s and is providing a fault level higher than this when using the 12 generators. I have never previously considered protection devices eg. fuses/CLIP in fault calculations as the calculation is performed first, then the protection devices are chosen to limit this.
Are there any reference to standards that you can think of that might make this clear? My calculations are for Australia, but I have been using IEC 60909 as this is the calculation method in software package PowerFactory.
At the power station, there are 12 generators that are connected on two separate buses (6 on each) that are inter-tied by a CLIP (current limiting protector). This CLIP works as a fuse and will operate at, lets say, 3kA. This will reduce the fault current at the power station and throughout the network. The clip can also be disconnected in order to operate as two independent buses. There are 2 feeders connected on each side of the bus and do not connect with each other downstream.
So when performing the maximum 3 phase fault calculations, should I be using the fault contribution for only the generators on the same side as the feeder? I am concerned because a busbar downstream is rated at 30kA for 1s and is providing a fault level higher than this when using the 12 generators. I have never previously considered protection devices eg. fuses/CLIP in fault calculations as the calculation is performed first, then the protection devices are chosen to limit this.
Are there any reference to standards that you can think of that might make this clear? My calculations are for Australia, but I have been using IEC 60909 as this is the calculation method in software package PowerFactory.