We designed a central cold air system, in which a radial fan with VFD is used to deliver 900 cfm at 50 inch static pressure. The air is to serve five outlets with 180 cfm each at 45 inch constant static pressure. Any of these five outlet can be closed by a butterfly damper any time, in other words, the system's load varies from 0 to 900 cfm any time. We installed a 4" manual relief damper at the end of the main duct, however, when all the five outlets are closed, the fan got problem even we open the 4" relief damper. The surging happened and the fan was making huge noise. We were trying to fix the problem by adding a bypss between the supply (discharge side of fan) and return air duct. I am thinking we need a heavy duty control valve at bypass that can modulate corresponding to the variable system load. However, what is the best way to control the valve, by pressure or by flow rate? Currently the static pressure at the end of the main duct is controlled by VFD... Thanks in advance for any suggestion and help.