Background: A cooling tower fan stack that is 18" tall. The fan is a 14' propeller fan with five blades.
There is of course a noticeable amplitude of vibration that occurs at blade pass frequency.A bump test indicates a natural frequency of about three times blade pass frequency.
Problem: The amplitude at three times the blade pass frequency is much higher than that occuring at blade pass frequency. Lesser amplitudes occur at 2,4,5,6 & 7 times blade pass frequency. I do not understand this as there is no exciting force at three times blade pass frequency.
Is the stack really vibrating at this amplitude and frequency or is it just an indication of the looseness of the stack.