Willard3 I respect your opinion but....
I may have stated the problem incorrectly lead you down the wrong path, I apologize. I want to limit the rise to 15 degrees. So, for a typical summer looking at 95F, you need about 210 CFM for every KW, therefore, revised heat loss of 220KW gives me about 46,200 CFM.
working out q=1.08cfm delta you get approx. the same thing. using 220kw~751,000btu/hr
thanks