> 1. The building consists of three different buildings
> ..
> and there is a door connecting building 1 to 2 and
> building 2 to 3.
If the doors are relatively "airtight" and are kept closed as much as possible then you only need to consider the one building you need to pressurize.
> 2. The control of pressure is of high importance here.
In that case I would take a fixed amount as the supply to the building and put a VAV-system in the exhaust.
Frequency-controlled fans on both AHU's. The VAV-valves would be controlled by a differentialpressure-sensor.
The frequency-control on the fans would be regulated to a constant pressure in the duct.
> What is the role of the A/C unit here?
> I need the room to be maintained at 75F all the time.
If by A/C-unit you mean the AHU: like I said, maintain the supply at constant flow, vary the supply-temperature to control the room-temperature.
> Specially that there are huge amounts of air
> supplied to(and exhausted from) the building,
> OTHER than the air supplied by the pressurization fan.
Are you talking about a separate fan just for pressurization? You do not need that if you already have an AHU for ventilating the building.
> 1. I am not sure if I understand your point about
> allowing 1-2 air changes/hr as a difference
> between supply and extraction.
Like Walkes says, you need to guess at the "leakiness" of the room/building. 1-2 air changes/hr is just my first guess.
If, for instance, you are already using 6 ac/hr for the ventilation/temperaturecontrol of the building then this could all end up leaking from the building at the desired pressure. Then there would be nothing left to do for you exhaust fan. If 1 or 2 air changes/hr is the leak-flow from the building then your exhaust system needs to take care of the remaining 4-5 ac/hr.
The calculation you make is indeed what I mean.
It's like this:
^ ^ leaks (unknown)
| |
------------------
fixed | room/building | variable
air supply --->| |---> exhaust
(AHU) | pressure build-up| (AHU)
| |
------------------