Failures and failure rates for 5MVAR transformers at 24hrs soak test
MacCB
Hi Lds & Gent's,
Can anyone out there refer to any report on the subject?
The only argument I've found is: "That is common recommendation from the trf vendors manual to complete a 24hrs soak test at commissioning".
But what kind of failures or malfunction would you reveal during this period, and especially after 23hrs, 59minutes and 59seconds?
BR
It is very hard to find any statistic during the short time range.
This number is expected to be relatively low in the region of infant mortality of the transformer.
A general idea of failure in this region is shown below.
Good luck
Trust the "soak test" means keeping the transformer energized at no-load. Clause 5.11 of IEEE C57.93-2019 Installation and maintenance of Transformers cover this procedure. This standard suggests 12 hours for energization without load for voltage classes 230 kV and above and 8 hours for below 230 kV. The purpose of this keeping under no-load is to is to limit damage from any fault arising from incipient defects from improper transport, storage or installation. Standard mentions " While this period of energization at no-load is not required, it is helpful to understand and evaluate the transformer in this condition prior to applying load" .I have experienced at least half a dozen cases of transformer failures during this soak test.