2 MVA Dry Type Tx.
27.6 kv./480 v. wye/wye
2 years old -30% loaded
Note:The transformer manufacturer completed the delta by using a #6 jumper wire instead of the interconnecting busbar they had used for the rest of this delta tertiary.
The wire melted and caused a phase to phase flashover.
We suspect the utility lost an incoming phase,when this failure occurred.
We will be looking at the upstream 27.6 kv. breaker protection settings and single phasing protection.