Dear all,
Has anyone used a trapezoidal wind load for a 6 m (20ft) facade in height? e.g. by calculating the wind load at 6 m and at the ground, and taking the trapezoidal load distribution... Is it allowed?
 
It is allowed in every wind code I've seen. Note that some wind codes have either a minimum magnitude design wind pressure or a minimum average wind pressure.

ASCE 7 even 'encourages' it by requiring the resultant force vector to be located at 55% of the height for certain structures (signs and freestanding walls)
 
Thank you for the reply.
Any experience with eurocode?
 
Only have used EC here and there, not enough to speak confidently about it.
 