Hi Pat,
I'm a bit more old school than my counterparts here, and like to go simple. I use very little non-contact microwave, have not used laser (as of yet), definitely not nuclear, and usually try to go cheap (my clients like it that way).
When you said that the switches are a little too coarse, what accuracy do you need, and what denomination do you need?
Usually, the problems with level measurement is temperature, corrosion, a second phase, or uneven surface. In your case, you already have a level switch that works (takes care of heat and corrosion), you didn't mention uneven surface or second phase. So, with that in mind, here are some food for thought:
1) More level switches. The problem often is you don't have any more "taps/nozzles" or you can't drill any more holes. So, maybe not so good.
2) Some point measurement switches have 2 or 3 points in the same unit. Magnetrol's point level switches, the Echotel line, has a dual point level switch (you get two levels in the same unit). You can use these in place of your single point units. The downside to this is that these are not side entry mounts, so you need holes on top. So, maybe something else.
3) A bridle with float and magnetic pickup. What material are you using now for your level switches? Use the same material for the bridle and float, and then use a magnetic pickup to send the 4-20 mA signal to your control system. I am assuming that molten salt has a fairly high density, so floats should work.
You didn't say where you are, but that's okay. I have recently dealt with Magnetrol on some water processing applications, and they have a wealth of knowledge when dealing with severe service. Might be worth a call to their rep/engineers.
Good luck.