extending coverage 15' into lower hazard

Status
Not open for further replies.

sac32079

Mechanical
May 27, 2011
18
When extending the coverage from the higher hazard 15' into the lower hazard, how do you separate the two systems? And am I allowed to use diferent k-factors in the lower hazard area? I have a warehouse with rack storage attached to an OH GP 2. Is there a way that I can avoid spacing into the lower hazard?
 
Replies continue below

Recommended for you

Draft curtains can be used to provide a physical separation between two different sprinkler systems in the same building.
 