For comparison, according to the spanish CTE at gas boiler rooms a weak (ejectable by the explosion) surface of
Surface (m2)=Volume (in m3) / 100
and not less than 1 m2
For example, a boiler room of 300 m3 would need 3 m2 of surface easily ejectable by the explosion.
Ventilation section needs not to be as much.
Source is RITE 2007 IT 1.3.4.1.2.3, in the code that by reference in CTE rules mechanical services design.