You can program the drive current to be whatever it is capable of, but generally that is going to be either 110% for 30 seconds or 150% for 60 seconds. So that will depend on how the drive was selected for the type of load. If it's a centrifugal pump or fan, it will likely be the 110% current for 30 seconds maximum. With that as the max current, you can plug that value into a Trandient Starting Analysis software program like SKM or ETAP if you want an exact value.
On the other hand, you can, if necessary, program the VFD to never exceed FLA of the motor and, assuming you never need more than Full Load Torque to accelerate, take all the time in the world to do so and not cause any more voltage drop than you would running the motor in the first place.