Expansion vessel

Status
Not open for further replies.

lorenzo67

Chemical
Dec 5, 2007
25
Hello at everybody,
I'm arranging a expansion vessel in a hot water circuit. Is there a rule for the velocity in the connecting pipe?

Thanks for collaboration
 
Replies continue below

Recommended for you

The expansion vessel is there to accommodate a water volume as the system heats up, so this is a slow process. You don't say what temperature you are operating at but assuming you operate at 80ºc you will get around a 10% volume increase. It is this volume that will flow through the pipe on heat up, when the system is at temperature there will be no flow through this pipe as the system will be at steady state condition.
Why is the velocity through the pipe so important?
What water volume is the system?
 
Sorry isn't important the velocity in the pipe but I need to know how the nozzle is sized.
 
Lorenzo, that's such a different question, I recommend starting a new thread. But first, determine exactly what you're trying to do.

Patricia Lougheed

******

Please see FAQ731-376: Eng-Tips.com Forum Policies for tips on how to make the best use of the Eng-Tips Forums.
 