Mar 4, 2011 #1 Dymalica Mechanical Joined May 4, 2007 Messages 43 Location US I looked through the forums and they get a lot into software. How do you manually calculate an expansion loop dimensions? Is there something in ASHRAE for this? An Example is 140 degree F water at 300 gpm in a 4" Black steel sch 40 pipe? Thanks
I looked through the forums and they get a lot into software. How do you manually calculate an expansion loop dimensions? Is there something in ASHRAE for this? An Example is 140 degree F water at 300 gpm in a 4" Black steel sch 40 pipe? Thanks
Mar 4, 2011 #2 ChrisConley Mechanical Joined May 13, 2002 Messages 975 Location CA ASHRAE HVAC Systems and Equipment 2008 S45.11. Whole section on expansion loops and calculations. Upvote 0 Downvote
Mar 4, 2011 #3 ChrisConley Mechanical Joined May 13, 2002 Messages 975 Location CA Need pipe length (anchor to anchor) to complete the calculation also. Upvote 0 Downvote
Mar 4, 2011 #4 ione Mechanical Joined Oct 22, 2009 Messages 1,344 Location IT http://thermacor.com/downloads/documents/15.103-4_001.pdf Regards Upvote 0 Downvote