I have tag, have the joist manufacturer helping me out (building is only 5 years old) but have the following questions:
Disclaimer - we do not typically deal with joists/joist girders or structures like this on a normal basis. We get them from time to time but I thought I'd reach out to get more information to educate myself a little more on this process.
1. We have manufacturer checking new load cases for us due to snow drifts at new RTU.
2. We provided new load cases on joists and joist girders.
3. We received output from manufacturer.
4. There are obvious areas that need reinforcing, but manufacturer is questioning how heavy our DL used is.
Design drawings indicate a specific DL used for the roof ballast, say 12 PSF. While on-site we observed anywhere from 2-3" of ballast on roof. We averaged 2-1/2" at 95 PCF - which is ~20 PSF DL. The 95 PCF is what is provided in AISC manual (and a few other locations) for "Stone, Quarried, Piled - Limestone". Anyone have any better documentation for anticipated density of roof ballast?
Obviously the original design was meant for 12 PSF, but based on our observations, and limited material information, we're coming up with a rather significant difference (especially when it comes to these joists, which have NO fat at all).
Thanks for any feedback!
RC
All that is necessary for the triumph of evil is that good men do nothing.
Edmund Burke
I have tag, have the joist manufacturer helping me out (building is only 5 years old) but have the following questions:
Disclaimer - we do not typically deal with joists/joist girders or structures like this on a normal basis. We get them from time to time but I thought I'd reach out to get more information to educate myself a little more on this process.
1. We have manufacturer checking new load cases for us due to snow drifts at new RTU.
2. We provided new load cases on joists and joist girders.
3. We received output from manufacturer.
4. There are obvious areas that need reinforcing, but manufacturer is questioning how heavy our DL used is.
Design drawings indicate a specific DL used for the roof ballast, say 12 PSF. While on-site we observed anywhere from 2-3" of ballast on roof. We averaged 2-1/2" at 95 PCF - which is ~20 PSF DL. The 95 PCF is what is provided in AISC manual (and a few other locations) for "Stone, Quarried, Piled - Limestone". Anyone have any better documentation for anticipated density of roof ballast?
Obviously the original design was meant for 12 PSF, but based on our observations, and limited material information, we're coming up with a rather significant difference (especially when it comes to these joists, which have NO fat at all).
Thanks for any feedback!