We are doing an expansion at a power plant. I have a 3x2 pile cap which is 3' thick w/ #8@12 E.W.:
X X X
X X X
which is apparently not good under the new loading conditions. (FWIW, it is not sufficient under the original loading either.)
I didn't have access to the original 1990 calculations, so I just took the value of the brace (or) connection could support to determine the lateral loading value. Original pile capacity was 120T. I have a new geo report which allows me to go up to 145T. I'm at capacity for these piles, so it doesn't surprise me the cap is insufficient (more so) by calculations.
The baseplate of the column is 2'-4" below top of slab (actually 2'-6" mat, not slab), and the pocket is filled with grout. My thoughts were to chip out the grout, weld (2) W24x103 along each column flange (W24 web to W14x145 column flange) Here goes:
W24
----- CL (Sym About)
|| W14 .
and set the flanges of the W24s on W18x143 frame work beneath the slab level. Grillage would likely better describe what I'm attempting to do. The flanges of the W24 will hit about 2" from the CL of the W18. I'm going to stiffen the W18 flanges substantially where this occurs. I'm spanning these W18s out to the edges of the original grout pocket. I will then be about 9" from the CL of the outside piles.
Has anyone out there done anything similar?
Anybody got a better idea? (please)
X X X
X X X
W24
|| W14 .