I have an existing concrete beam, and it is over stressed in shear, but not moment for the new load.

I have a very limited depth, so I was going to attach to the bottom of the beam with a WT and say that the shear would all be carried by the WT.

Is this acceptable? I was going to try to make the section composite, but the shear flow I get is way to high for any kind of post-installed anchors.

I cannot connect to the sides of the existing beam because there are cast-in-place joists framing into it.

If I assume that the beams act separately than the load would all go to the concrete beam and it would not work. I was thinking about it from a limit state approach. i have more shear strength (using the two sections) than applied so it is ok.

 
Replies continue below

Recommended for you

I was going to suggest something similer to Einsteim. For the jacks, you could use permanent grouted Fressinet flat jacks.
 