@Ed,lets simplify it for you. the volume we are talking about here is the volume of the building to be ventilated. so in your case, Area x Height: 7276 sqft x 29.92 ft= 217,698 cuft
Since you are not clear in your design intent, For a simple ware house, a.06 cuft/min per sqft(ASHRAE std) of the ware house is use here so you needed a fan or fans with a 436.56 CFM approx; 450 CFM,you may needed two @ 250 CFM each. but this is not enough to conclude that it meets your requirements. if you consider occupancy, then 5 person per 1000 sqft,means you have to to consider 15 people, are they smoker? like other friends here, if you consider the PEL, you may use the air change method too.
Next, How do you convey the air to the fan,with duct or without,if ducted,calculate the static pressure necessary to overcome the air resistance in the ductworks.
Hope that helps