I'd like to revisit the whole issue of instantaneous current for efficient motors.
I read EASA's "Principles of Large AC Motors" copyright 2000, page 2-32, which provides discussion leading up to the changes in NEC for energy efficient motor. There are mentioned two properties of energy efficient motors:
#1 - they tend to have locked rotor current
#2 - they tend to have higher L/R ratio's.
That is the extent of any explanation I can discern from this publication concerning the reason for increased instantaneous settings on high-efficiency motors.
Here is my interpretation of the significance of these statements:
A - #1 has an obvious effect on instantaneous trip, although for design B my understanding is the limits on LRC still hold.
B - #2 has the effect that the dc component will decay less in the first half-cycle so the peak inrush current can get closer to the max theoretically possible inrush current of 2*sqrt(2)*LRC.
So in energy efficient motors the increase of peak inrush above LRC will likely be higher than in others (due to higher X/R), but still not above 2.0*sqrt(2)*LRC..... at least that's my understanding from what I've read.
But I certainly still could be missing something. Everything in the two links above seems to fit together except for the statement at
that: "The peak value of inrush current, which can be as high as 20 times rated current, will be different each time the equipment is energized due to residual magnetism in the core."
I am skeptical of this statement. There is certainly variability on inrush current due to the closing angle with respect to voltage which is not even mentioned. While significant residual magnetism theoretically has the ability to push the core farther into saturation upon application of voltage and therefore could
theoreticallyincrease peak inrush current, I have never heard that mentioned elsewhere.
Any thoughts?