Continue to Site

Eng-Tips is the largest engineering community on the Internet

Intelligent Work Forums for Engineering Professionals

  • Congratulations waross on being selected by the Eng-Tips community for having the most helpful posts in the forums last week. Way to Go!

exceeding top concrete cover

Status
Not open for further replies.

salman85

Geotechnical
Dec 23, 2011
25
what will you do if found pedestal with top concrete cover say about 120 mm (while the design state that concrete cover 50mm) ? This condition raise after do core drill to take a sample..
 
Replies continue below

Recommended for you

It depends. A picture would help. What do you mean by a "pedestal"? What is the function of the reinforcement?
 
Two issues with that. The anchor bolts will have reduced development length with the pedestal verticals, and the top of the pedestal is unreinforced for lateral forces imparted by the column base. Whether or not this creates an unsatisfactory condition depends on the forces involved.
 
Status
Not open for further replies.

Part and Inventory Search

Sponsor