The rocket scientist inquires"
"Maybe the question should be "Why did EVAPCO decide to offer PWT with their products (cooling towers), and include a factory warranty", which by the way is a better warranty than if the client choose to use a traditional water treatment?"
Ev**** response when your cooling tower fills up with scale:
Sorry to hear about that, here is your money back on the $1,000 magnet system. No, we will not acid wash the cooling tower to remove the scale, that is not covered by the warranty, that is consequential damages and will cost you a lot more than the magnet system.
The tradition water treatment supplier warrantee is that he will fix the water treatment equipment such that it operates within design parameters. If you purchased a cooling system that was designed properly, the cooling tower will not scale when operating within design paramaters.
"I would assume that EVAPCO could be considered an independent, qualifed, disinterested, third party, since it is their equipment that they are putting it on. Maybe they got tired of providing a warranty for their cooling towers when using traditional water treatment? If traditional water treatment was working so well, why would they look into PWT?"
Ev***** response: You are required to operate the cooling tower within the parameters. If you operate outside the water treatment parameters, the warranty on the cooling tower is voided.
Corrosion and Scale Control
To control corrosion and scale, the water chemistry of the recirculating water must be maintained within certain parameters. The specific measures required vary from system to system and are dependent on the chemistry of the make-up water, the metallurgy of the piping and heat transfer devices exposed to the recirculating water, and the temperatures at which the system will be operating. Bleed/blowdown, the continuous flow of a small portion of the recirculating water to a drain, is used to control the concentration of dissolved solids. On rare occasions this may be adequate to control scale and corrosion. More often, however, chemical scale and corrosion inhibitors are necessary, which raise the allowable level of dissolved solids without the risk of scale and corrosion.
Chemically treated water should be kept within the guidelines given in Table 7. In cases where bleed/blowdown alone is being employed for corrosion and scale control, without chemical treatment, your water treatment specialist may recommend more conservative limits than those shown in Table 7.
Table 7 – Typical Quality Guidelines for Chemically Treated Circulating Water
Property of Water Recommended Level
pH 6.5 to 9.0*
Hardness as CaCO3 30 to 750 ppm2
Alkalinity as CaCO3 500 ppm maximum2
Total Dissolved Solids 1500 ppm maximum
Conductivity 2400 micromhos3
Chlorides 250 ppm maximum as Cl 410 ppm maximum as NaCl
Sulfates 250 ppm maximum
Silica 150 ppm maximum
"I could be wrong..."
Yes you are.
"Why is Evapco the only cooling tower company selling magnets?"
Even a broken clock indicates the correct time twice a day