RJB32482
Chemical
- Jan 19, 2005
- 271
We are looking at evacuating an underground pentane line by pulling a vacuum on it like evacuating refrigerant from a compressor system. I am looking at what vacuum we have to pull on it to get it to "vaporize" and get pulled from the system. So what do I look at for pentane. My thought was the vapor pressure of pentane at ambient conditions. So if the vapor pressure at 60 F is 10 psia, then would we need to pull at least 4.7 psi of vacuum on the pipeline to get it evacuated?
Or how would I compare it to the refrigerant (vapor pressures of both)? So if the vapor pressure of the refrigerant is lower than pentane, then we could pull the same vacuum and be able to get the pentane out of the pipe.
Any thoughts on this method. We are going to steam the pipe also to get the pentane out of the creases in the carbon steel pipe to do hot work on it.
Thanks.