trosepe
Electrical
- Mar 28, 2009
- 82
A local solar contractor (really nice guy)has installed a 15KW PV system on the property of a multi-millon dollar home. There has been some type of dispute and the owner is requesting an engineer to inspect the system for compliance to 2005 NEC.
The inverter output circuit connects to an 80 amp, 2 pole circuit breaker in the 400 amp service with 400 amp main.
Section 690.64 (B)(2) states that the sum of the overcurrent devices supplying power to a bus or cable shall not exceed the rating of the bus or cable.
The exception for dwellings states that the sum of the overcurrent devices shall not exceed the 120% percent the rating of the bus or cable.
Note the absence of the word 'supplying power' in the exception. If you go by the words in the exception - this guy is in trouble.
It seem obvious to me that the authors of this artical intended the exception to allow 120 percent of the overcurrent devices 'supplying power' but that is not what it says.
He can't derate the system and use a smaller circuit breaker as his contract sets an output level that requires the 80 amp circuit breaker.
Since this will be likely litigated, and we all know how lawyers are about what the words say and not what they really intended; what do you all think? Did the the code authors leave out the 'supplying power'in the exception as a mistake or intentionally?
The inverter output circuit connects to an 80 amp, 2 pole circuit breaker in the 400 amp service with 400 amp main.
Section 690.64 (B)(2) states that the sum of the overcurrent devices supplying power to a bus or cable shall not exceed the rating of the bus or cable.
The exception for dwellings states that the sum of the overcurrent devices shall not exceed the 120% percent the rating of the bus or cable.
Note the absence of the word 'supplying power' in the exception. If you go by the words in the exception - this guy is in trouble.
It seem obvious to me that the authors of this artical intended the exception to allow 120 percent of the overcurrent devices 'supplying power' but that is not what it says.
He can't derate the system and use a smaller circuit breaker as his contract sets an output level that requires the 80 amp circuit breaker.
Since this will be likely litigated, and we all know how lawyers are about what the words say and not what they really intended; what do you all think? Did the the code authors leave out the 'supplying power'in the exception as a mistake or intentionally?