Has anyone seen or remember Equivalent Length published values for Internal Valve with integrated Excess Flow Valves used on LPG tanks. Size of these valves would range from 1-1/2" to 5". I already have values for fittings, Ball/Globe and Check valves.
If you know the EFVs Cv you should be able to calculate the equivalent length. The attached links seem to have pretty good equivalent length calculators.
Vzeos-The EFV is like a restriction inside the internal valve to the tank and I found no data such as the coefficient factor K that would allow me to determine head loss. I may have to guesstimate. Installation of EFV's on propane tanks is fairly new material in the NFPA 58. Perhaps I should check out Ammonia tank safety devices.
chicopee- I'm familiar with EFVs. We've used them in natural gas service lines for many years... Most manufacturers of flow components can provide you with the component capacity in terms of a Cv value from wich you can calculate the K value from K=891*d^4/(Cv^2) (see Crane page 3.4).
vzeos- Is your formula for the K value derived for a specific gravity of one? I don't have crane but I'll check out my mechanical and chemical handbooks.
chicopee- I would recommend getting a copy of Crane Technical Paper No. 10, if you can... K is independent of fluid and specific gravity... In the formula, Cv expresses flow rate in gallons per minute of 60 F water with 1.0 psi pressure drop across the valve.