abfer, there are two effects that become more and more significant at very low Rpm/Hz. The first is motor slip rate. At higher Rpm motor slip is only really a nuisance from the efficiency and power loss point of view. At 1 Hz the slip rate will be significantly higher than the actual motor shaft speed, so the motor will stop (under load) long before you reach zero Hz.
The other effect is motor winding resistance. At high voltage and frequency there will be a voltage drop across the internal resistance of the windings. That is also just a nuisance and efficiency issue at higher speeds.
At very low drive Hz, the ac drive voltage will also be very low, but maybe with still up to full load current. The resistive voltage drop becomes larger and larger as a proportion of the available motor drive voltage.
The result being, that at very low frequencies you are going to require more Hz and more drive volts in order to sustain sufficient torque to do the job. In other words speed/load characteristics may be very poor.
The more sophisticated variable frequency drives allow compensation for these two effects, but that may still not be sufficient.
Some sort of active feedback control may be the answer, because the performance of an open loop system could leave rather a lot to be desired. A lot depends on what level of performance you require.