I have had a discussion come up a few times and have yet to come to a clear consensus between engineers on the correct approach for designing elongated pedestals to support equipment. I’m curious if anyone here has dug into this and could help clarify the best approach for this type of design problem. All the references below refer to section in ACI 318-14 unless noted otherwise.
For the purpose of having a reference, and a situation where I’ve seen this before, I’ll imagine I need to support a horizontal vessels with a saddle support about 7’-6” in length. For this, assume the pier supporting the saddle will be 8’ long x 1’6” wide x 4’ tall. The saddle bears continuously across the pier so the gravity loads will be, for simplicity, evenly distributed over the pier’s cross-section.
Initially, my first instinct is to jump into ACI Chapter 10 which includes provisions for the design of columns and reinforced concrete pedestals. Section 10.6.1.1 requires an area of longitudinal steel to be a minimum of 0.01Ag unless the gross area of the pedestal is larger than necessary to resist the loads in which case the minimum area can be reduced to 0.005Ag per 10.3.1.2 which is common for these types of structures. Finally, 10.7.3.1 requires the longitudinal reinforcement be at least (4) longitudinal bars within rectangular ties.
So based on this I would need at least 0.005Ag longitudinal steel which would result in several vertical bars spaced along each face of the pier within a rectangular tie. The additional transverse reinforcement requirements would then kick in per 10.7.6.1.2 which leads to 25.7.2.3. 10.7.6.1.5 goes on to say all longitudinal reinforcement shall be laterally supported with ties unless analysis shows otherwise. Ultimately to limit going into additional detail the pedestal would need to have several vertical bars with a rectangular tie around the perimeter, ties providing confinement at the anchor bolts per 10.7.6.1.6, and interior cross-ties to satisfy the tie spacing requirements for laterally supporting vertical bars per 25.7.2.
Looking through the code, it appears to me that these types of support structures in many cases could qualify as a wall which might be designed without the perimeter and cross-ties to support longitudinal reinforcement in the wall. “Wall is defined in ACI as a vertical element designed to resist axial load, lateral load, or both, with a horizontal length-to-thickness ratio greater than 3, used to enclose or separate spaces. So the definition with the exception of enclosing/separating a space is met. If we then went to Chapter 11, we could find that the minimum longitudinal reinforcement could be as low as 0.0012 from Table 11.6.1 if the axial loads are below the calculated Pn value. This chapter goes on to state in 11.7.4.1 (errata 9th printing) if lateral reinforcement is required for compression and if Ast exceeds 0.01Ag, longitudinal reinforcement shall be laterally supported by transverse ties. Since we would not meet this criteria the addition of lateral ties per 25.7.2 wouldn’t be required. So from this approach you could have quite a bit less required reinforcement in the wall since the area of longitudinal steel would be less, the perimeter tie is not called out and the cross-ties are not required. I would still assume the ties for anchor confinement would need to be provided per 10.7.6.1.6.
My approach has always been to treat this as a column designed to Chapter 10. Any thoughts from anyone here on reasons the second approach can/should not be followed?
For the purpose of having a reference, and a situation where I’ve seen this before, I’ll imagine I need to support a horizontal vessels with a saddle support about 7’-6” in length. For this, assume the pier supporting the saddle will be 8’ long x 1’6” wide x 4’ tall. The saddle bears continuously across the pier so the gravity loads will be, for simplicity, evenly distributed over the pier’s cross-section.
Initially, my first instinct is to jump into ACI Chapter 10 which includes provisions for the design of columns and reinforced concrete pedestals. Section 10.6.1.1 requires an area of longitudinal steel to be a minimum of 0.01Ag unless the gross area of the pedestal is larger than necessary to resist the loads in which case the minimum area can be reduced to 0.005Ag per 10.3.1.2 which is common for these types of structures. Finally, 10.7.3.1 requires the longitudinal reinforcement be at least (4) longitudinal bars within rectangular ties.
So based on this I would need at least 0.005Ag longitudinal steel which would result in several vertical bars spaced along each face of the pier within a rectangular tie. The additional transverse reinforcement requirements would then kick in per 10.7.6.1.2 which leads to 25.7.2.3. 10.7.6.1.5 goes on to say all longitudinal reinforcement shall be laterally supported with ties unless analysis shows otherwise. Ultimately to limit going into additional detail the pedestal would need to have several vertical bars with a rectangular tie around the perimeter, ties providing confinement at the anchor bolts per 10.7.6.1.6, and interior cross-ties to satisfy the tie spacing requirements for laterally supporting vertical bars per 25.7.2.
Looking through the code, it appears to me that these types of support structures in many cases could qualify as a wall which might be designed without the perimeter and cross-ties to support longitudinal reinforcement in the wall. “Wall is defined in ACI as a vertical element designed to resist axial load, lateral load, or both, with a horizontal length-to-thickness ratio greater than 3, used to enclose or separate spaces. So the definition with the exception of enclosing/separating a space is met. If we then went to Chapter 11, we could find that the minimum longitudinal reinforcement could be as low as 0.0012 from Table 11.6.1 if the axial loads are below the calculated Pn value. This chapter goes on to state in 11.7.4.1 (errata 9th printing) if lateral reinforcement is required for compression and if Ast exceeds 0.01Ag, longitudinal reinforcement shall be laterally supported by transverse ties. Since we would not meet this criteria the addition of lateral ties per 25.7.2 wouldn’t be required. So from this approach you could have quite a bit less required reinforcement in the wall since the area of longitudinal steel would be less, the perimeter tie is not called out and the cross-ties are not required. I would still assume the ties for anchor confinement would need to be provided per 10.7.6.1.6.
My approach has always been to treat this as a column designed to Chapter 10. Any thoughts from anyone here on reasons the second approach can/should not be followed?